[Ticket Question] 4 Zone Fire Alarm With 2 Outputs Required?
Started by Secware, Feb 02 2012 01:09 PM
3 replies to this topic
#2
Posted 02 February 2012 - 01:10 PM
I need 2 outputs on the Fire Alarm because there is currently a door on an lectric release on the only output that is available on their current firealarm. I need the second output for another door that we have installed an electric release and keypad entry onto.
#3
Posted 02 February 2012 - 01:11 PM
Use any 4 zone panel and then use 2 fire relays for your two outputs.
I can recommend Cranford:
http://www.securityw...4box-p-242.html
I can recommend Cranford:
http://www.securityw...4box-p-242.html
#4
Posted 02 February 2012 - 09:54 PM
As above wire the single fire output to 2 external relays. Then use each relay for the desired purpose.